  #1  
Old 01-19-2012
gcyeaw's Avatar
gcyeaw gcyeaw is offline
Gardner
 
Join Date: Dec 2007
Location: Ridgewood
Posts: 6,128
Default Honda 2000i ground

I installed a Progressive Industries surge protector this summer before leaving on an extended trip. I never tested it with my Honda 2000i backup generator, however.

Today I fired up the Honda, connected it to my 30 amp shore line (which is wired with a 50 amp RV end so it feeds both sides of the panel) and waited for the Progressive to time out and connect. Then I noticed an error code indicating there was an open ground. I did some ohm meter checking and found the Honda does not tie the neutral to ground. I looked it up on-line and found in the manual where it states this. The Progressive will not connect the power if the ground is open. Also, I tried the manual override and the contactor started to oscillate on and off very quickly, not a good thing. I suspect it is related to the open ground problem and will work properly once I address the grounding situation.

So now I know I need to make a special adapter for the Honda that ties the neutral to ground when used with the coach. Electrical code requires the ground and neutral to be connected at only one point, which is generally the power source (generator). But if you were connecting it to your house, the ground and neutral are connected in your main panel (the power source), so it would be improper for the generator to make that connection as well.


Without the Progressive Industries unit I would not have known the connection was not made. It would likely not be an issue unless I took the extra step to ground the generator to the earth via the provided screw connector. Then I would have a hot chassis situation.

As Rosanne Rosanadanna says, "It's always something"
__________________
Gardner Yeaw
83FC35 SB $IXTEEN TON$
Ridgewood, New Jersey
Travel Blog http://newdealblog.com/archives/category/trek-2012
Reply With Quote
  #2  
Old 01-19-2012
Randy Dupree's Avatar
Randy Dupree Randy Dupree is offline
Forum owner
 
Join Date: Dec 2007
Location: Archer,Fl
Posts: 19,337
Default

Rosanne Rosanadanna,thats a name i have not heard in a long time!
__________________
Randy Dupree
2000 LXI 43
Bainbridge,Ga.
Archer Fl.
www.buybyebluebird.com

randy@randydupree.com
Reply With Quote
  #3  
Old 01-20-2012
GreenBird's Avatar
GreenBird GreenBird is offline
Senior Member
 
Join Date: Oct 2010
Location: Trufant (stump fence capital)
Posts: 831
Default

I'm guessing you won't have a hot chassis because the generator's enclosure is nonconductive. Seems meaningless to have 3-prong outlets on the generator unless they are grounded. Am curious how your neutral bonded adapter plug works out - hope you let us know.
__________________
Leonard Campbell
Trufant, MI
1986 PT40
Reply With Quote
  #4  
Old 01-20-2012
gcyeaw's Avatar
gcyeaw gcyeaw is offline
Gardner
 
Join Date: Dec 2007
Location: Ridgewood
Posts: 6,128
Default

Quote:
Originally Posted by GreenBird View Post
I'm guessing you won't have a hot chassis because the generator's enclosure is nonconductive. Seems meaningless to have 3-prong outlets on the generator unless they are grounded. Am curious how your neutral bonded adapter plug works out - hope you let us know.
I have been thinking about it and realized there is a very simple way to acomplish the ground-neutral connection without any trouble. The Honda has a duplex outlet. I can wire a 20 amp plug with the neutral and ground connected and plug it into one of the outlets. That will tie the neutral and ground together within the Honda. Then I will plug my standard 20 amp to 30 amp adapter into the second outlet.

When using the Honda with the RV I employ my 20 to 30 amp adapter and my 30 to 50 amp shore line. It should work using the special plug in the other side of the duplex outlet and I will not have to worry that I might forget and use a modified adapter elseware.
__________________
Gardner Yeaw
83FC35 SB $IXTEEN TON$
Ridgewood, New Jersey
Travel Blog http://newdealblog.com/archives/category/trek-2012
Reply With Quote
  #5  
Old 01-20-2012
tulipvendor50 tulipvendor50 is offline
Senior Member
 
Join Date: Dec 2007
Location: Terrace,
Posts: 1,053
Default Honda 2000i ground

Gardner:
See you are a genius right LOL. Keep thinking and you never know what you will come up with.
I will have to keep this in mind as I was thinking of buying a small genset as well.
__________________
Bill
1988 40WB XXV "Anniversary Special Edition"
http://tulipvendor50.blogspot.ca/
Kitimat, B.C. Canada eh
Reply With Quote
  #6  
Old 01-20-2012
Turbokitty's Avatar
Turbokitty Turbokitty is offline
Timberlake Products
 
Join Date: Apr 2008
Location: Clearwater
Posts: 3,289
Default

Quote:
Originally Posted by Randy Dupree View Post
Rosanne Rosanadanna,thats a name i have not heard in a long time!
http://www.youtube.com/watch?v=Z7gLJr03vNQ
__________________

Ryan and Michelle Saari
1983 FC35RB
1985 PT36
Clearwater, Florida
Reply With Quote
  #7  
Old 01-21-2012
racin41bb's Avatar
racin41bb racin41bb is offline
Senior Member
 
Join Date: Feb 2008
Location: Roanoke
Posts: 594
Default

We have a Coleman Powermate 1500/1800 watt portable "camping" generator that was purchased in 2001. There is a "neutral floating" label on top of the generator. Must be common to most portables. Gardner, thanks for bring up the potential problems (and solutions).

By managing the circuit breakers we are able to operate all the 120VAC systems with the exception of the roof air & electric heaters. It will operate the water heater as long as the WH is the only load.

Bill B.
__________________
Bill & Rita in Roanoke, VA
"IRON HOUSE"
1987 FC-35SB ('87 factory demo)
Cat 3208ATAAC-300
12.5kw Kohler/Yanmar (w/slide)
"Magic carpet made of steel"
Steve Goodman 1970

"You never fail until you stop trying".
Reply With Quote
  #8  
Old 01-22-2012
GreenBird's Avatar
GreenBird GreenBird is offline
Senior Member
 
Join Date: Oct 2010
Location: Trufant (stump fence capital)
Posts: 831
Default

I have a portable gennie and sure enough neutral is not bonded to chassis ground. I'm thinking this is because they anticipate you might connect it to a building where the neutral/ground bond already exists. I agree that if this is your only power source and neutral is not bonded elsewhere it should be done at the gennie as Gardner suggested.

The Bird has neutral bonded at the gennie not the breaker box. When you switch to shore power neutral is not bonded in the coach - it should be at the supply as required by code. When you powered with an unbonded gennie you were truly unbonded. Your surge suppressor did you a favor by not allowing it - in fact it couldn't work like that. Seems to me you need to ground the gennie to make the suppressor functional. Code doesn't require earth ground on portable generators but in the case of a surge suppressor it needs a drain for overvoltage.
__________________
Leonard Campbell
Trufant, MI
1986 PT40
Reply With Quote
  #9  
Old 01-24-2012
gcyeaw's Avatar
gcyeaw gcyeaw is offline
Gardner
 
Join Date: Dec 2007
Location: Ridgewood
Posts: 6,128
Default

I made up a plug connecting ground to neutral and tried it out on the Honda. IT WORKED AS DESIGNED. The Progressive surge protector/ power management unit showed no errors and engaged the power to the coach.

So all I need to do when using the Honda 2000i as a power source for the coach is plug the ground-neutral shorted plug in one side of the generator duplex outlet and the 20 to 30 amp adapter into the other and I am good to go.

Pics show the plug, how it is wired and installed in the generator.
Note-the copper colored connection in the plug is the HOT and has no connection. The ground and silver colored terminal, which is the neutral, are shorted using 14 guage solid wire.
Attached Thumbnails
Click image for larger version

Name:	ShortingPlug-1.jpg
Views:	74
Size:	86.0 KB
ID:	14656   Click image for larger version

Name:	ShortingPlug-2.jpg
Views:	87
Size:	89.6 KB
ID:	14657   Click image for larger version

Name:	ShortingPlug-3.jpg
Views:	79
Size:	154.8 KB
ID:	14658  
__________________
Gardner Yeaw
83FC35 SB $IXTEEN TON$
Ridgewood, New Jersey
Travel Blog http://newdealblog.com/archives/category/trek-2012
Reply With Quote
Reply

Bookmarks

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
Ground disconnect? Butch Charpentier Electrical 4 01-02-2012 02:30 PM
Honda EU 2000i inverter use??? Bravo Electrical 29 10-09-2011 09:36 PM
Blueox base plate for a 2003 Honda Element warbucks13477 Towbars, Hitches and Braking Systems for your Toads, etc. 0 10-03-2011 06:18 PM
Toad Honda Odyssey Suska General 11 08-30-2010 09:37 PM