Default Generator won't run

15kw power tech, starts well but will only run if you hold the start switch down.replaced the oil and water shut down switches and also jumper end them to test, no difference. I replaced all four relays in the control box. I can manually hold the fuel rack linkage open and it will run but no power to the solenoid after releasing the start switch. Generator end works fine, must be electrical, what am I missing?
__________________
Robert Briggs
Mims, FL
1993 40WB
Reply With Quote
  #2  
Old 03-17-2015
CaptPegLeg CaptPegLeg is offline
Senior Member
 
Join Date: Jun 2013
Location: Kitty Hawk
Posts: 910
Default

stop solenoid?
__________________

Bob Sumners
1993 WB
1983 PT35 Sold
Reply With Quote
  #3  
Old 03-17-2015
Randy Dupree's Avatar
Randy Dupree Randy Dupree is offline
Forum owner
 
Join Date: Dec 2007
Location: Port St Joe,Fl
Posts: 35,600
Default

does the rad fan run when the gennys running?
voltage regulator is my suspect.
__________________
DO NOT SEND PM
email me at randy@randydupree.com only.

Randy Dupree
2000 LXI 43
Bainbridge,Ga.
Port St Joe Fl.
www.buybyebluebird.com

randy@randydupree.com
Reply With Quote
  #4  
Old 03-17-2015
REB REB is offline
Member
 
Join Date: Jan 2015
Location: Mims
Posts: 65
Default Gen won't run

Yes fan starts and runs when generator starts. 120 both legs power is good. It had been intermittent before this, run for an hour max then shut off. The last time it shut down I jumped the oil shut down switch and it restarted. On recommendation of power tech I replaced the relays and safety switch, now stumped.
__________________
Robert Briggs
Mims, FL
1993 40WB
Reply With Quote
  #5  
Old 03-17-2015
StiehlBird's Avatar
StiehlBird StiehlBird is offline
Member
 
Join Date: Dec 2013
Location: Sequim
Posts: 65
Default

Try Aux Battery switch on dash. Will tie engine bank to coach battery bank. if gen crank powered from engine bank and gen fuel solenoid from coach bank, you will have problem you describe. Tie banks together long enough to charge all batteries.
I installed digital battery voltage indicator in bedroom where I had watched TV too long on inverter one night.
__________________
Christopher Stiehl
Fulltime
1992 WBWL 40
"Wanderlust"
stiehlcj@gmail.com
Reply With Quote
  #6  
Old 03-17-2015
REB REB is offline
Member
 
Join Date: Jan 2015
Location: Mims
Posts: 65
Default Gen won't run

Batteries and power are good. Generator starts right up and will run fine as long as I hold the start button down. The second I release the start button the solenoid on the fuel rack loses power and the engine shuts down. The other "hot" wire to yhe solenoid never energizes and thus the shut down.i just can't trace this wire back and my drawings don't match the relay colors.
The generator ac output is perfect when running and all the gauges read normal.
Randy mentioned voltage regulator, located ? End of generator or in the box on back of gen?
__________________
Robert Briggs
Mims, FL
1993 40WB
Reply With Quote
  #7  
Old 03-17-2015
REB REB is offline
Member
 
Join Date: Jan 2015
Location: Mims
Posts: 65
Default

If I run a 12volt jumper to the solenoid to keep it running for the hour I need to get down the road until I can diagnose the problem am I going to hurt anything other than bypassing the safeties?
__________________
Robert Briggs
Mims, FL
1993 40WB
Reply With Quote
  #8  
Old 03-17-2015
Matt Morehart Matt Morehart is offline
Junior Member
 
Join Date: Oct 2014
Location: Woodland
Posts: 29
Default

Reb,

This happened to me last month on my '95 WB40. We couldn't locate the problem after several attempts over a few days. Then I pushed the reset button on the generator and the problem stopped. I don't know if I had a surge problem from the shore power line, but now I disconnect power from the shore line when I start the generator to be safe.

BTW, my generator blower fan just quit and the gen won't run the AC- so Im going to test the blower motor to see what up.

Hope this helps.
__________________
Matt Morehart
Woodland, California
'95 40WB
Reply With Quote
  #9  
Old 03-17-2015
REB REB is offline
Member
 
Join Date: Jan 2015
Location: Mims
Posts: 65
Default

Forgot to say but yes I tripped and rest the breaker on genset and also disconnected shore power with same result.
Reply With Quote
  #10  
Old 03-17-2015
Matt Morehart Matt Morehart is offline
Junior Member
 
Join Date: Oct 2014
Location: Woodland
Posts: 29
Default

Reb,

When I described the problem to Power Technology Southeast (352)365-2777, the mfg of my generator, they said it sounded like an oil pressure sensor or water temperature sensor problem. We never had to go that far.
__________________
Matt Morehart
Woodland, California
'95 40WB
Reply With Quote
Reply

Bookmarks

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
87 FC Generator dlefty Generators 95 07-28-2019 05:45 PM
12 KW Generator cemjam FC (Forward Control Unique Issues) 9 06-24-2014 01:46 PM
LXI Generator Johnny M Slone Generators 9 07-15-2013 07:02 PM
New Generator????? Jcmaynot Generators 13 12-02-2012 03:58 PM
generator raywaco Generators 5 06-21-2010 04:48 PM

Web Search:

All times are GMT -4. The time now is 07:34 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2019, vBulletin Solutions Inc.