Default Ground Fault

When attempting to connect my 1999 LXi to shore power, if the shore power is protected with a Ground Fault outlet/breaker, the ground fault immediately trips. I turned off all breakers in coach, turned off the inverters and the ground fault still trips immediately. Any ideas?
__________________
Greg Peterson
1999 LXI 43'
Ridgefield, CT
Reply With Quote
  #2  
Old 09-06-2009
davidmbrady
Guest
 
Posts: n/a
Default

You have a neutral to ground connection somewhere in your coach. Turn off all power sources, disconnect the house and chassis batteries, and ohm out the ground and neutral wires at any 120V receptacle. The resistance should be infinite, open circuit, if its small (a few ohms) then you have a ground to neutral short somewhere.
Reply With Quote
  #3  
Old 09-06-2009
sanibel's Avatar
sanibel sanibel is offline
Complete Greenhorn
 
Join Date: Jun 2008
Location: Sanibel
Posts: 894
Default

Lots of good posts on how to sort out which circuit by pulling whites off the panel. Search for "GFCI"
__________________
John (and Robin) Churchill
Black Tongue Farm
Sanibel, FL

1979 FC33 Buddy Luce's bus (looking for a name)

LARGE MARGE - She left me for another man
Reply With Quote
  #4  
Old 09-06-2009
iamflagman's Avatar
iamflagman iamflagman is offline
(1943-2018) Forum Co-founder/Administrator
 
Join Date: Dec 2007
Location: Hopkins
Posts: 11,506
Default

Quote:
Originally Posted by sanibel View Post
Lots of good posts on how to sort out which circuit by pulling whites off the panel. Search for "GFCI"

Alway look down below the thread on the forum, near the bottom of the page and you will see "Similar Threads" listed sometimes, they are posted there because a key word in the question asked triggers an automatic search on that word, sometimes they are a good source for the answer, but not always, here is what is listed there;

Chassis ground question

Another ground problem?

Another ground issue

Electrical ground and neutral
__________________

JOHN FINN
FORUM MODERATOR-ADMINISTRATOR
1982 FC35RB
I'm NO EXPERT, but I did stay in the FINN'S INN EXPRESS last night
HOPKINS, SOUTH CAROLINA
VISIT THE FINN'S INN EXPRESS REMODELING ADVENTURE AND TECH. TIPS
I'M SO SLOW ON THE HILLS,THAT I GET TO SMELL THE FLOWERS AS I GO BY.....AND WATCH THEM GROW TOO!! NOT SO MUCH ANYMORE
Visit the WILD HARE RACING website
REMEMBER 9/11
Reply With Quote
  #5  
Old 09-06-2009
GregRP GregRP is offline
Junior Member
 
Join Date: Aug 2009
Location: Ridgefield
Posts: 24
Default

I turned off the Main Breakers in the load center and turned off the breakers from the inverters yet it still tripped the ground fault. It seems to me the the fault has to be between the shore power plug and the load center; therefore, disconnecting whites will not help.

I believe that I heard somewhere that the Safeline System that warns if the shore power is connected to a reverse polarity source can trip a ground fault. Is this true? If so, how can I prevent it from tripping a ground fault?

My original thought was that I could find the fault by turning on breakers one at a time until the ground fault tripped. Unfortunately, it tripped with all breakers off including the two mains.
__________________
Greg Peterson
1999 LXI 43'
Ridgefield, CT
Reply With Quote
  #6  
Old 09-06-2009
davidmbrady
Guest
 
Posts: n/a
Default

I don't think turning off breakers is sufficient. You have to disconnect neutral wires.
Reply With Quote
  #7  
Old 09-06-2009
fxdwg fxdwg is offline
Senior Member
 
Join Date: Mar 2008
Location: okc
Posts: 3,843
Default

Turning off the breakers only shuts off the black wire, the neutral and ground are ALWAYS connected. You have to look further as already described.
__________________
John
96 WTOS 42'
OKC USA!


don't waste your time with a usa-spec ipod adapter- poor products with poor support
Reply With Quote
  #8  
Old 09-06-2009
GregRP GregRP is offline
Junior Member
 
Join Date: Aug 2009
Location: Ridgefield
Posts: 24
Default

Have you tried connecting to a ground fault protected shore connection with your '02? I believe we have similar electrical systems.
__________________
Greg Peterson
1999 LXI 43'
Ridgefield, CT
Reply With Quote
  #9  
Old 09-06-2009
sanibel's Avatar
sanibel sanibel is offline
Complete Greenhorn
 
Join Date: Jun 2008
Location: Sanibel
Posts: 894
Default

The circuit breaker only interrupts the black power or hot wire. You have an incorrect connection (a short) between the white wire and the green somewhere. Disconnect all 120V power. You can confirm the short by checking the ohms between the white buss bar and the ground buss bar in the breaker box. It should read infinite, but yours will be a low number. Start pulling the white wires off the bus bar (you do not need to worry about which one goes to which spot) until you get an infinity reading. Leave that one disconnected. Reconnect each white (except the last/bad one) checking after each to be sure there are not 2 problem circuits.

Now trace the bad white and find its black partner which you will then trace to a circuit breaker. Disconnect the black from the circuit breaker. It is not hot anymore Plug the bus back in to shorepower and it should be OK. Start hunting for the short on the known bad circuit. Heating elements are a known problem- block heater and pipe tapes, water heater element. There can also be a bad connection n a outlet box where the white is touching the metal box and shorting to ground.
__________________
John (and Robin) Churchill
Black Tongue Farm
Sanibel, FL

1979 FC33 Buddy Luce's bus (looking for a name)

LARGE MARGE - She left me for another man
Reply With Quote
  #10  
Old 09-06-2009
curtsprenger's Avatar
curtsprenger curtsprenger is offline
Senior Member
 
Join Date: Jan 2008
Location: Anaheim Hills, CA
Posts: 3,863
Default

Quote:
Originally Posted by GregRP View Post
When attempting to connect my 1999 LXi to shore power, if the shore power is protected with a Ground Fault outlet/breaker, the ground fault immediately trips. I turned off all breakers in coach, turned off the inverters and the ground fault still trips immediately. Any ideas?
I'm going to assume the coach has been connected to a shore GF outlet prior to today without tripping the GF. Right? The problem might be in the shore cord male end.
__________________
Curt Sprenger
1987 PT38 8V92 "MacAttack Racing"
1974 FC31 534 gas engine, air brakes (sold)
Anaheim Hills, Calif.
Do Not Send PM (Private Messages) Please
curtsprenger@gmail.com
Reply With Quote
Reply

Bookmarks

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
Chassis ground question GPSGary Electrical 7 03-26-2009 06:33 PM
Another ground problem? gcyeaw Electrical 2 03-09-2009 04:17 PM
Another ground issue gcyeaw Electrical 1 02-14-2009 08:59 PM
Electrical ground and neutral gcyeaw Electrical 2 07-30-2008 09:48 PM
Camp Ground Membership jlq Craigs List, Ebay, Coaches and other Finds 1 04-21-2008 11:06 PM

Web Search:

All times are GMT -4. The time now is 09:07 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2019, vBulletin Solutions Inc.