Default NEWBIE AC PROBLEM

Here are the symptoms: Running generator and three roof A/C and interior lights. Gauges over entry door read as follows: AC voltage leg 1: 140 volts. Leg 2 : 110 volts... Amps leg1 :0 & Leg 2: 41 amps. Thought maybe gauges were wrong so tested duplex outlets, some read read 110 others 140. Turned off each air and checked gauges as each shutdown ; only leg 2 ammeter dropped off. Not sure if this is related to only having some duplexes hot when plugged into 20 amp. Wondering if transfer switch is what I should be looking at. Can any of you gurus help me out?
__________________
Elliot Harris

95 WLWB 40' SOLD!

"RARA AVIS"

Morristown, Tennessee

FMCA #F27720
Reply With Quote
  #2  
Old 09-07-2009
davidmbrady
Guest
 
Posts: n/a
Default

Elliot,

I don't think there's anything wrong. It looks like you have 2 AC's on one leg and one on the other, and for whatever reason, only the 2 AC's on leg 2 were running when you looked at the Ampere gauges. Maybe the AC on leg one was short cycling or maybe it's compressor wasn't running and only the fan was blowing. I'm assuming that there are devices that you can turn on to get a deflection on leg one's ampere gauge? If not, then the gauge may be bad. The thing is that the genny is powering two legs that are relatively unbalanced. You have inductive loads on each, but twice the reactance on leg 2. This causes the current and voltage to be out of phase on leg one, and greatly out of phase on leg 2. This puts a large strain on the generator, which is trying hard to produce "in phase" current and voltage. The outcome is 110V on leg one and 140V on leg 2. If you want to be easy on your generator try running only 1 AC on each leg, and use your third AC judiciously.
Reply With Quote
  #3  
Old 09-07-2009
fxdwg fxdwg is offline
Senior Member
 
Join Date: Mar 2008
Location: okc
Posts: 3,843
Default

Elliot,

While I don't get that much difference in voltages, I do get a mild voltage difference when running the AC's. There's 2 on one leg and one on the other and it does show up soemtimes kind of weird on the meters. Start by getting power on and stable with nothing on, both legs should be equal. Then start turning on 1 AC at a time and note what the meters do. You can then figure out what combination to run them in to minimize problems.
__________________
John
96 WTOS 42'
OKC USA!


don't waste your time with a usa-spec ipod adapter- poor products with poor support
Reply With Quote
  #4  
Old 09-07-2009
catshreds's Avatar
catshreds catshreds is offline
Senior Member
 
Join Date: Jul 2009
Location: Roscoe
Posts: 1,397
Default

Unfortunately when all three acs were off,the voltages still read 110 & 140 with the gen running. I'm concerned about plugging any appliance in to one of the 140 volts by mistake.
__________________
Elliot Harris

95 WLWB 40' SOLD!

"RARA AVIS"

Morristown, Tennessee

FMCA #F27720
Reply With Quote
  #5  
Old 09-07-2009
fxdwg fxdwg is offline
Senior Member
 
Join Date: Mar 2008
Location: okc
Posts: 3,843
Default

Sounds like the regulator in the genny needs some work.
__________________
John
96 WTOS 42'
OKC USA!


don't waste your time with a usa-spec ipod adapter- poor products with poor support
Reply With Quote
  #6  
Old 09-07-2009
catshreds's Avatar
catshreds catshreds is offline
Senior Member
 
Join Date: Jul 2009
Location: Roscoe
Posts: 1,397
Default

Not to confuse the issue, but one more anomaly: with gen and shore power disconnected. inverter on, some duplexes are hot others are dead, including (unfortunately),the one that the bat chargers are plugged into! I'm trying to find the common denominator to all this.
__________________
Elliot Harris

95 WLWB 40' SOLD!

"RARA AVIS"

Morristown, Tennessee

FMCA #F27720
Reply With Quote
  #7  
Old 09-07-2009
Rick's Avatar
Rick Rick is offline
Senior Member
 
Join Date: May 2009
Location: Bellefonte
Posts: 13,226
Default

I wouldn't think you would want the battery charger outlet hot when running on your inverter.
__________________
Rick Shawver
1SG Ret
2000 LX
Vise Grips
Bellefonte, AR
F127656
Reply With Quote
  #8  
Old 09-07-2009
davidmbrady
Guest
 
Posts: n/a
Default

That's right, inverter/charger operation should be exclusive or. The receptacles that are dead may not be wired up to the inverter.
Reply With Quote
  #9  
Old 09-07-2009
gcyeaw's Avatar
gcyeaw gcyeaw is online now
Gardner
 
Join Date: Dec 2007
Location: Ridgewood
Posts: 8,852
Default

If the charger was powered by the inverter, which itself is powered by the batteries, you would be asking the batteries to charge themselves. If you can make that work, patient it.
__________________
Gardner Yeaw
86 PT-36 Golden Memories
83FC35 SB $IXTEEN TON$ SOLD
78 FC 33 Happinest (Sold)
Ridgewood, New Jersey
Reply With Quote
  #10  
Old 09-07-2009
catshreds's Avatar
catshreds catshreds is offline
Senior Member
 
Join Date: Jul 2009
Location: Roscoe
Posts: 1,397
Default

perpetual energy machine! Now THAT would be a useful option!!
__________________
Elliot Harris

95 WLWB 40' SOLD!

"RARA AVIS"

Morristown, Tennessee

FMCA #F27720
Reply With Quote
Reply

Bookmarks

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
Newbie question catshreds HVAC, Air Conditioners, Aqua Hot, Primus, Webasto, Chassis Heaters, Furnaces and Water Heaters 3 08-24-2009 07:31 PM
Newbie looking to buy his first BB catshreds New Members 17 07-15-2009 11:18 AM
Newbie, and a question on length folivier New Members 3 09-21-2008 08:07 PM
Newbie Here crr First-Timers and Newcomers 3 03-10-2008 04:29 PM
Newbie to this site jlq New Members 1 12-17-2007 09:13 AM

Web Search:

All times are GMT -4. The time now is 04:26 PM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2019, vBulletin Solutions Inc.