  #1  
Old 07-27-2015
gcyeaw's Avatar
gcyeaw gcyeaw is offline
Gardner
 
Join Date: Dec 2007
Location: Ridgewood
Posts: 8,849
Default My Progressive overregisters

My progressive cut the power from my generator today registering it as 131 and 133 volts respectively on the two hot leads. I believe the 133 is the progressive trip point. I checked with my Fluke meter and it says 126.7 I trust the fluke.

I have noticed a difference in the past when using the meter vs the progressive display, but it didn't cause any problems so I forgot about it. But now that the generator is running an 126/127 the Progressive is killing the power. I can bypass the progressive protection with the switch on the remote for now, but I will contact Progressive and see if it can be adjusted or replaced. They are good about customer care, so let's hope for the best.

There is no adjustment that I know of on the regulator on the Kohler, but there is a clear material visible on one edge and I can see a little potentiometer inside the material. It doesn't look like it was intended for user access.
__________________
Gardner Yeaw
86 PT-36 Golden Memories
83FC35 SB $IXTEEN TON$ SOLD
78 FC 33 Happinest (Sold)
Ridgewood, New Jersey
Reply With Quote
  #2  
Old 07-27-2015
mrkane mrkane is offline
Senior Member
 
Join Date: Jan 2008
Location: USA
Posts: 212
Default

Gardner:

Didn't you recently post a scope waveform from your generator showing a non-sinusoidal trace? While the Fluke may be true RMS, the Progressive voltage could be affected by the spikes. Is the generator still showing this problem?

(Could the voltage spikes come from slip-ring/brush problems? I had a Kohler break the brushes due to the slip-rings becoming elliptical from wear.)


--M.R.Kane
1987 PT40 'Sleipnir'
currently Iron River, MI
Reply With Quote
  #3  
Old 07-28-2015
Dieselbird01's Avatar
Dieselbird01 Dieselbird01 is offline
John Wyatt – Administrator/Moderator
 
Join Date: Feb 2008
Location: Titusville
Posts: 3,896
Default

Quote:
Originally Posted by gcyeaw View Post
My progressive cut the power from my generator today registering it as 131 and 133 volts respectively on the two hot leads. I believe the 133 is the progressive trip point. I checked with my Fluke meter and it says 126.7 I trust the fluke.

I have noticed a difference in the past when using the meter vs the progressive display, but it didn't cause any problems so I forgot about it. But now that the generator is running an 126/127 the Progressive is killing the power. I can bypass the progressive protection with the switch on the remote for now, but I will contact Progressive and see if it can be adjusted or replaced. They are good about customer care, so let's hope for the best.

There is no adjustment that I know of on the regulator on the Kohler, but there is a clear material visible on one edge and I can see a little potentiometer inside the material. It doesn't look like it was intended for user access.
Hi Gardner,

I snipped these lines from the “Voltage Regulator Bench Test and Adjustment” procedure that was in my 12.5 kW Kohler Troubleshooting guide… Perhaps they apply to the pot you found.. perhaps not? Proceed at your own risk.

If regulator adjusting Pot (See Figure 3) has not been factory sealed, set Pot to its mid position.


If regulator Pot has been factory sealed, carefully remove sealer and turn Pot slider so slider works freely. Set Pot. to mid position.

Disconnect generator from load. Connect voltmeter across L0 and L1. Start engine. Adjust regulator Pot. so meter shows proper output voltage. Stop engine. Remove voltmeter and seal Pot with RTV or suitable substitute.

I sent a condensed version of the 12.5 kW Kohler Troubleshooting guide to John Finn a few years ago… he posted it here if you want to see the whole bench test and adjustment procedure:

http://www.wanderlodgeownersgroup.com/forums/attachment.php?attachmentid=1096&stc=1&d=123181487 1


Quote:
Originally Posted by mrkane View Post
Gardner:

Didn't you recently post a scope waveform from your generator showing a non-sinusoidal trace? While the Fluke may be true RMS, the Progressive voltage could be affected by the spikes. Is the generator still showing this problem?

(Could the voltage spikes come from slip-ring/brush problems? I had a Kohler break the brushes due to the slip-rings becoming elliptical from wear.)


--M.R.Kane
1987 PT40 'Sleipnir'
currently Iron River, MI
The same thought crossed my mind ...
Attached Thumbnails
Click image for larger version

Name:	Voltage reg.jpg
Views:	329
Size:	88.2 KB
ID:	37032  
__________________
John Wyatt
Titusville, Florida
1991 40' WLWB-WTB
Body Number F095567
My Location: http://www.bbirdmaps.com/user1.cfm?user=4

1991 40' WB ...From 2008 - Present
1984 ½ PT-36 .From 2000 - 2008
1973 FC-31 .....From 1991 - 2001
Reply With Quote
  #4  
Old 07-28-2015
gcyeaw's Avatar
gcyeaw gcyeaw is offline
Gardner
 
Join Date: Dec 2007
Location: Ridgewood
Posts: 8,849
Default

Quote:
Originally Posted by mrkane View Post
Gardner:

Didn't you recently post a scope waveform from your generator showing a non-sinusoidal trace? While the Fluke may be true RMS, the Progressive voltage could be affected by the spikes. Is the generator still showing this problem?

(Could the voltage spikes come from slip-ring/brush problems? I had a Kohler break the brushes due to the slip-rings becoming elliptical from wear.)


--M.R.Kane
1987 PT40 'Sleipnir'
currently Iron River, MI
I noticed the same thing on shore power( voltage, not the anomaly) , but it was a while ago. I need to hook up and do some checking.
__________________
Gardner Yeaw
86 PT-36 Golden Memories
83FC35 SB $IXTEEN TON$ SOLD
78 FC 33 Happinest (Sold)
Ridgewood, New Jersey
Reply With Quote
Reply

Bookmarks

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
Saved by the Progressive gcyeaw Electrical 17 05-06-2015 07:12 PM
Progressive EMS install Dennis&Ella Electrical 19 07-24-2013 01:47 PM
Progressive Education innovative1 GOT CLEAN JOKES...add them here!! (MODERATED) 0 10-24-2011 10:08 AM
Progressive Industries Surge Protector White Hat Guy RV Products Review 7 07-23-2011 11:14 PM
Progressive Industries EMS AC7880 Electrical 7 07-06-2010 08:34 PM

Web Search:

All times are GMT -4. The time now is 04:19 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2019, vBulletin Solutions Inc.