Default Overheated Perkins

Well, after 14k miles of trips and a hundred or more hours on the generator since I last had an issue, it quit today. Just what I needed at the start of the big trip. It's 97 and all ac's were on. We are boondocking at Greenbelt NP. I had to start the engine to bring up the air so I could open the draw. I need a hand pump for emergencies

I started it and the fan ran but it shut down right away. I popped the wire off the high temp switch and it ran fine I shot the high temp switch area and it was well over 200. I checked the rest of the parts of the system and it was much cooler. I figured that when it shut down the area at the rear of the ending heated up from residual heat. Anyway, after disconnecting the switch and starting the gen, it ran fine and cooled down to 160 pretty quickly. I left the draw open.

So why did it get hot? I felt the air from the fan and it seems to exit the top and sides of the shroud mostly, with little coming out the rear of the shroud. There is no blockage and if I recall this is the way it has always been. I suspect that since I insulated the compartment, the insulation is close to the side and top of the shroud and is probably interfering with the flow. I need to remove it around the fan and shroud area. I will do that and see if the issue is resolved.

For now the draw is partially open and the over temp switch is back in the circuit.
__________________
Gardner Yeaw
86 PT-36 Golden Memories (sold)
83FC35 SB $IXTEEN TON$ SOLD
78 FC 33 Happinest (Sold)
Ridgewood, New Jersey
Reply With Quote
  #2  
Old 07-03-2012
Buckeye Bird's Avatar
Buckeye Bird Buckeye Bird is offline
Senior Member
 
Join Date: Jan 2008
Location: Lancaster
Posts: 2,479
Default

Glad it was something fairly obvious and an easy fix. Our Powertech shut down on us from getting too hot a few weeks back when running just the 2 A/C's in 95 degree heat. We ended up using the same solution-opening it up a little to facilitate better air flow and all was fine. I am going to try and clean out the radiator fins this week before heading to Wilmington to see if that helps. It is supposed to be around 100 on Sat.
__________________
Dan & Janet
Buckeye Bird II
1994 BMC 37'
2018 Wrangler Unlimited
Lancaster, Ohio
Reply With Quote
  #3  
Old 07-03-2012
birds_first's Avatar
birds_first birds_first is offline
RV Appraiser
 
Join Date: Jan 2008
Location: Louisville, KY
Posts: 5,694
Default

I would say it is just that time to replace the high temp switch. After all these years it is bound to fail. Just think of how many times it has expanded and contracted over its lifetime. This time it just went a little further and did its job. At least you were not on the road and you were able to figure it out fairly quickly. Question should be how did Cathy hold up? Two years ago in 100+ degree in South Dakota a breaker failed on mine and you would thought it was 1000 the way Fran carried own. I still hear it today
__________________
John McGinnis, former USAF EOD
95WB42MD S60, Mid-Entry "B-Rex" For Sale
88FC35 (SOLD)
Louisville, KY/Jeffersonville, IN
2000 Jeep Cherokee "Franicon"
Retired: Auctioneer, RE Broker, and Certified Vehicle & Heavy Equipment Appraiser
"Dead man walking"
502-417-5681
Reply With Quote
  #4  
Old 07-04-2012
gcyeaw's Avatar
gcyeaw gcyeaw is offline
Gardner
 
Join Date: Dec 2007
Location: Ridgewood
Posts: 9,037
Default

Quote:
Originally Posted by birds_first View Post
I would say it is just that time to replace the high temp switch. After all these years it is bound to fail. Just think of how many times it has expanded and contracted over its lifetime. This time it just went a little further and did its job. At least you were not on the road and you were able to figure it out fairly quickly. Question should be how did Cathy hold up? Two years ago in 100+ degree in South Dakota a breaker failed on mine and you would thought it was 1000 the way Fran carried own. I still hear it today
John,
One reason I was so quick to try the temp sensor is that the old one failed two years ago. It took a few minutes longer to figure it out back then. I already have a new one installed.

Kathy's first words were "How far is it from here to that generator guy in Pennsylvania?"
__________________
Gardner Yeaw
86 PT-36 Golden Memories (sold)
83FC35 SB $IXTEEN TON$ SOLD
78 FC 33 Happinest (Sold)
Ridgewood, New Jersey
Reply With Quote
  #5  
Old 07-04-2012
sfedeli's Avatar
sfedeli sfedeli is offline
Senior Member
 
Join Date: Jan 2008
Location: Sinking Valley
Posts: 3,597
Default

Gardner- Could it have been the capacitor on the fan motor? Was the fan blowing when it shut down? I have a spare 220V fan motor in the shed that came off John Ely's '86 PT40. It will work on your Perkins too. You're about 2 hours away. Call if you want to take it along on the trip just in case.
__________________
Shane Fedeli
85PT40
Sinking Valley, PA

"That which you most need to find will be found where you least want to look"
shanefedeli@gmail.com
717-645-4912
Reply With Quote
  #6  
Old 07-04-2012
gcyeaw's Avatar
gcyeaw gcyeaw is offline
Gardner
 
Join Date: Dec 2007
Location: Ridgewood
Posts: 9,037
Default

Shane,
The fan is running full speed as far as I can tell. I have restarted the gennie several times with no issues. A new cap is easy to find if needed. A new motor is a bit tougher, but I have no space to put it Thanks for the offer, however.

I cut away a block of insulation along side the fan shroud area and closed the draw, so far it is running 160 degrees, but it isn't that hot out yet. It ran three hours last evening with the draw open about 8 or 10 inches. No overheat issue yet. It's gonna wait till we get to the Ohio Mile and the ambient temp goes to 100+ outside
__________________
Gardner Yeaw
86 PT-36 Golden Memories (sold)
83FC35 SB $IXTEEN TON$ SOLD
78 FC 33 Happinest (Sold)
Ridgewood, New Jersey
Reply With Quote
  #7  
Old 07-04-2012
davidmbrady
Guest
 
Posts: n/a
Default

Gardner,

The Powertech's have a squirrel cage fan mounted at the back of the enclosure designed to keep some minimum amount of airflow passing over and around the generator head. We also have remote mounted radiators which keeps the heat away for the genny head. From what I'm reading, it sounds like the radiator, fan, and shrouding is in good shape and working properly. It sounds like there's excess heat in the area of the over-temp shutdown switch which I think is coming from the genny head. Any chance of installing a squirrel cage fan to get more ventilation into and out of the genny enclosure?
Reply With Quote
  #8  
Old 07-04-2012
gcyeaw's Avatar
gcyeaw gcyeaw is offline
Gardner
 
Join Date: Dec 2007
Location: Ridgewood
Posts: 9,037
Default

Quote:
Originally Posted by davidmbrady View Post
Gardner,

The Powertech's have a squirrel cage fan mounted at the back of the enclosure designed to keep some minimum amount of airflow passing over and around the generator head. We also have remote mounted radiators which keeps the heat away for the genny head. From what I'm reading, it sounds like the radiator, fan, and shrouding is in good shape and working properly. It sounds like there's excess heat in the area of the over-temp shutdown switch which I think is coming from the genny head. Any chance of installing a squirrel cage fan to get more ventilation into and out of the genny enclosure?
David,
I need to look into that. It's pretty tight in the gennie compartment, but perhaps some re-arranging might help. If I moved the battery to a different place it would be easier. I have room in my new battery tray, but need to locate the aux relay where I could make the new battery connection to get back to the genny compartment.
__________________
Gardner Yeaw
86 PT-36 Golden Memories (sold)
83FC35 SB $IXTEEN TON$ SOLD
78 FC 33 Happinest (Sold)
Ridgewood, New Jersey
Reply With Quote
  #9  
Old 07-04-2012
davidmbrady
Guest
 
Posts: n/a
Default

You know what to do... Maybe something like a remote mounted sucker fan with race-car brake style duct work connected to an opening at the top/rear of the enclosure, with natural convection currents working in your favor.
Reply With Quote
  #10  
Old 07-04-2012
gcyeaw's Avatar
gcyeaw gcyeaw is offline
Gardner
 
Join Date: Dec 2007
Location: Ridgewood
Posts: 9,037
Default

OK, it crapped out again. The fan stopped. I opened the high temp switch and it starts and puts out AC, but the fan doesn't run. Is there a thermal switch on the fan motor? That could be tripping, or it has another problem. But since it puts out AC I am conficent the generator and voltage regulator are OK.

Trying to contact Shane to get the motor he has..but it is the evening of the 4th after all....We will head for Hershey in the morning if I can get in touch with Shane.
__________________
Gardner Yeaw
86 PT-36 Golden Memories (sold)
83FC35 SB $IXTEEN TON$ SOLD
78 FC 33 Happinest (Sold)
Ridgewood, New Jersey
Reply With Quote
Reply

Bookmarks

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
Perkins 12.5KW injectors ryoung Parts Wanted 10 01-02-2011 01:25 PM
BMC Overheated 1st time/TPS issues AC7880 BMC (Bluebird Motor Coach Unique Issues) 21 07-24-2010 04:01 PM
Another Perkins question Friday1 Generators 7 04-09-2010 10:40 PM
Perkins question Friday1 Generators 4 04-09-2010 03:19 PM
Leaky Perkins AuctionIndy Generators 7 11-01-2008 10:44 AM

Web Search:

All times are GMT -4. The time now is 03:33 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2023, vBulletin Solutions Inc.