Default 12.5 Kubota/Yanmar generator stops

****. I'm not too proud... I usually can figure stuff out if I beat my head on it long enough. But this has me stumped and before I spend big bucks I want to see if I can get some renewed direction from the experts. I've poured over REALLY good and informative posts here on site on figuring these things out but still no luck getting this thing back running. Anyway, here is my problem.

I have a '86 PT40. Arguably the finest motorcoach every made by man. The generator is Kohler/Yanmar 12.5. It has run reliably for years. 4 or 5 years ago I replaced the 230v cooling fan with modern 12v. It has worked since without issue. That is the only modification. The other day I started it (I try and start every 2-3 weeks regardless) and after running for a few seconds, shut itself off by de-energizing the fuel solenoid.

Battery condition is excellent.
Oil level good.
Coolant level good.
Engine starts almost instantly and strong which is typical until shut-down, 3-5 seconds.
I have unhooked engine sensors one at a time and same shut down.
I have pulled control box and checked for loose terminals.
I have cleaned and properly reattached grounding strap.
I replaced the (3) Bosch relays. The existing ones were metal cased and just appeared old.
I did not replace the high voltage relay which appeared to be in excellent condition.
I can force engine to run by hold back fuel cut-off solenoid. When I do this the generator IS producing power as indicted on the front dash high voltage gages. The rocker start switch light DOES NOT illuminate.
If I hold back the solenoid for longer than 30-45 seconds, the engine sputters a bit but continues running. I haven't keep running longer than that.

I hope there are some clues that might lead to a solution. Perhaps a diagnostic I have overlooked.
Any questions please ask and thanks in advance for any help or direction.

Robert
__________________
Robert Jenkins
1986 PT40
"FLTRSK"
Austin, Texas
Reply With Quote
  #2  
Old 04-06-2017
racin41bb's Avatar
racin41bb racin41bb is offline
Senior Member
 
Join Date: Feb 2008
Location: Roanoke
Posts: 733
Default

Our '87 FC had a intermittently open wire in the harness. Generator is on a slide and flexing over time may have caused the open circuit. We rewired around the open wire. A subsequent problem involved several cannon connectors. I replaced most of the pins in the plugs & sockets and rewired the ones that connected directly to the control box.

I don't know if this will help since you are producing power by holding the fuel solenoid in the run position--our unit did not produce power either time we had generator issues.

Bill
__________________
Bill & Rita Brinner in Roanoke, VA
"IRON HOUSE"
1987 FC-35SB ('87 factory demo)
Cat 3208ATAAC-300
12.5kw Kohler/Yanmar (w/slide)
"Magic carpet made of steel"
Steve Goodman 1970

"You never fail until you stop trying".
Reply With Quote
  #3  
Old 04-06-2017
BobsBus BobsBus is offline
Senior Member
 
Join Date: Oct 2014
Location: Fort St. James
Posts: 97
Default

If the light in the start/stop switch does not come on, the engine safety system does not know the oil pressure came up, or thinks the coolant is over temp.

You may have to jump the senders instead of disconecting them to find the problem. Some systems use a loss of current to signal a fault, others use a closing switch to signal a problen.

The short run time is that the safety shut down system is overriden during cranking for a short time.

Just a few thoughts for you.

On my 1985 PT, I need to keep the start switch held down until the switch light comes on to keep the motor running. If I release the switch before the light comes on, the generator motor stops.
__________________
Bob Fritchey
Fort St. James, BC
1985 PT 40 BB
Reply With Quote
  #4  
Old 04-06-2017
K Ridley K Ridley is offline
Senior Member
 
Join Date: Mar 2010
Location: Spokane
Posts: 433
Default

It sounds like the 11 pin ice cube relay is not working. When this relay receives 120 volts it closes contacts to turn on the switch lights and energize the hold in on the fuel solenoid. You should be able to start it without the cover on the control box and see if the relay is activating.
__________________
Kevin Ridley
1979 FC35 XV (Sold!)
1986 PT40 Amazing Grace (Full Timing It)
Follow our travels at:
ampersandgemandjewelry
Reply With Quote
  #5  
Old 04-06-2017
Blue Emu's Avatar
Blue Emu Blue Emu is offline
Senior Moments
 
Join Date: Feb 2012
Location: Where ever we park our bus.
Posts: 1,002
Default

Quote:
Originally Posted by K Ridley View Post
It sounds like the 11 pin ice cube relay is not working. When this relay receives 120 volts it closes contacts to turn on the switch lights and energize the hold in on the fuel solenoid. You should be able to start it without the cover on the control box and see if the relay is activating.
I had this exact problem on the desert of Quartzsite. The 120v relay sees power from the head, closes, and then all of the other safety relays are activated. Even when it LOOKS like it is closing properly, if one of the contacts is corroded or not making a good contact, the engine will stop.

I replaced my 120v relay (Thanks to a neighbor at Q who had one), and all is happy once again. Based on my experience, I would go there first.
__________________

John & Aleda Ellsworth
A wide-body, living in a narrow bus.
1985 FC-35-SB "Color Us Gone"
john.m.ellsworth@gmail.com
Reply With Quote
  #6  
Old 04-07-2017
trystero trystero is offline
Senior Member
 
Join Date: Jan 2009
Location: austin
Posts: 134
Default

Thank you all so much for the info. I'll get on it and report back!
__________________
Robert Jenkins
1986 PT40
"FLTRSK"
Austin, Texas
Reply With Quote
  #7  
Old 04-15-2017
trystero trystero is offline
Senior Member
 
Join Date: Jan 2009
Location: austin
Posts: 134
Default

Kevin, you nailed it Buddy. It was the 11-pin "ice cube" relay. It looked to be in good order but replaced and now all good. Thanks to all for the feedback!
__________________
Robert Jenkins
1986 PT40
"FLTRSK"
Austin, Texas
Reply With Quote
Reply

Bookmarks

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
Kubota Generator ghost PetKos Generators 1 12-05-2016 04:07 PM
Kubota diesel 17.5 generator asking $3K NH Bill Parts and Other Items For Sale 4 08-06-2015 09:33 PM
Generator starts/stops ku4ns Generators 19 10-13-2012 01:21 PM