Default GENERATOR Yanmar/Kohler

After the trip to the beach i got home and now the generator wont start. As soon as i try to start it it blows the 10 amp fuse in the control box. I have removed the starter had it tested it is fine replaced grounds and found that if i hold the fuel solenoid in by hand i can start it and it runs fine even after i let go of the solenoid it stays in. So i got a new one but still same problem if you are looking at the solenoid when i try to start it as soon as the solenoid fully opens the fuse blows.
I have the early style according the book i have 12.5 Kohler with yammar engine.
__________________

John wheeler 86 pt38
Hanford,CA
Reply With Quote
  #2  
Old 05-18-2011
gcyeaw's Avatar
gcyeaw gcyeaw is offline
Gardner
 
Join Date: Dec 2007
Location: Ridgewood
Posts: 8,875
Default

John.
It still may be starter solenoid. I had exacticaly the same problem. The internal contacts are worn and the larger contact isn't making a good contact. That results in the starter trying to draw current through the S terminal, and that blows the fuse.

I did a write up, I will see if i can find it. Here are a couple of pics. I rotated the contact 180 degrees to provide a fresh contact surface for the solenoid washer. I also reversed the washer to provide a clean surface.
Attached Thumbnails
Click image for larger version

Name:	RearCoverOff.jpg
Views:	336
Size:	444.5 KB
ID:	10374   Click image for larger version

Name:	Rotated contact.jpg
Views:	335
Size:	467.4 KB
ID:	10375  
__________________
Gardner Yeaw
86 PT-36 Golden Memories
83FC35 SB $IXTEEN TON$ SOLD
78 FC 33 Happinest (Sold)
Ridgewood, New Jersey

Last edited by gcyeaw; 05-18-2011 at 08:24 PM.
Reply With Quote
  #3  
Old 05-19-2011
john wheeler john wheeler is offline
Senior Member
 
Join Date: Nov 2008
Location: Hanford
Posts: 81
Default

Gardner,
I thought the same thing but if reach in and push the plunger in on the fuel solenoid and hold it. I can reach back with my other hand push the start switch and it starts just fine.
__________________

John wheeler 86 pt38
Hanford,CA
Reply With Quote
  #4  
Old 05-19-2011
Randy Dupree's Avatar
Randy Dupree Randy Dupree is offline
Forum owner
 
Join Date: Dec 2007
Location: Port St Joe,Fl
Posts: 35,889
Default

Gardner is right.holding the plunger intakes the load off the starter solenoid and the fuse.
__________________
DO NOT SEND PM
email me at randy@randydupree.com only.

Randy Dupree
2000 LXI 43
Bainbridge,Ga.
Port St Joe Fl.
www.buybyebluebird.com

randy@randydupree.com
Reply With Quote
  #5  
Old 05-29-2011
john wheeler john wheeler is offline
Senior Member
 
Join Date: Nov 2008
Location: Hanford
Posts: 81
Default

Update i had the starter rebuilt, and it made no difference,still blowing the fuse . I did find that if i unplugged the four pin wiring harness from the control box,i could crank the generator up but would not stay running. So i replaced the regulator, now the generator starts but wont stay running and does not blow the fuse. From what i can see looking at the wiring diagram there is a relay made by guardian electric "A410-3666186-151" that takes 120 ac signal to activate a 12 volt relay. That keeps fuel solenoid open.This relay is a 12 pin so I'm not sure how to test it and i have had no luck locating it on the great world wide web.
__________________

John wheeler 86 pt38
Hanford,CA
Reply With Quote
  #6  
Old 05-30-2011
racin41bb's Avatar
racin41bb racin41bb is offline
Senior Member
 
Join Date: Feb 2008
Location: Roanoke
Posts: 729
Default

John,

There is another fuse (8 amp) under the generator cover just a above the regulator.
__________________
Bill & Rita Brinner in Roanoke, VA
"IRON HOUSE"
1987 FC-35SB ('87 factory demo)
Cat 3208ATAAC-300
12.5kw Kohler/Yanmar (w/slide)
"Magic carpet made of steel"
Steve Goodman 1970

"You never fail until you stop trying".
Reply With Quote
  #7  
Old 05-30-2011
thomas_sorrentino's Avatar
thomas_sorrentino thomas_sorrentino is offline
Senior Member
 
Join Date: Jan 2008
Location: Bedford Hills, NY
Posts: 923
Default

Quote:
Originally Posted by john wheeler View Post
Update i had the starter rebuilt, and it made no difference,still blowing the fuse . I did find that if i unplugged the four pin wiring harness from the control box,i could crank the generator up but would not stay running. So i replaced the regulator, now the generator starts but wont stay running and does not blow the fuse. From what i can see looking at the wiring diagram there is a relay made by guardian electric "A410-3666186-151" that takes 120 ac signal to activate a 12 volt relay. That keeps fuel solenoid open.This relay is a 12 pin so I'm not sure how to test it and i have had no luck locating it on the great world wide web.
John,
If you hold the fuel solenoid in, will the generator stay running? If so when you do that are you getting 120 VAC and is the cooling fan running?
__________________
Tom Sorrentino
1987 PT38
Bedford Hills, NY
Westchester Sandblast
Reply With Quote
  #8  
Old 05-30-2011
Randy Dupree's Avatar
Randy Dupree Randy Dupree is offline
Forum owner
 
Join Date: Dec 2007
Location: Port St Joe,Fl
Posts: 35,889
Default

Most rebuild shops never look at the starter solenoid,if it works it works,so they assume.
Not saying thats still your problem,just saying that it could still be a problem.
On that 12 pin relay,i have seen a wire come off one of the pins,check all the wires.
__________________
DO NOT SEND PM
email me at randy@randydupree.com only.

Randy Dupree
2000 LXI 43
Bainbridge,Ga.
Port St Joe Fl.
www.buybyebluebird.com

randy@randydupree.com
Reply With Quote
  #9  
Old 05-30-2011
Dieselbird01's Avatar
Dieselbird01 Dieselbird01 is offline
John Wyatt – Administrator/Moderator
 
Join Date: Feb 2008
Location: Titusville
Posts: 3,915
Default

Quote:
Originally Posted by john wheeler View Post
Update i had the starter rebuilt, and it made no difference,still blowing the fuse . I did find that if i unplugged the four pin wiring harness from the control box,i could crank the generator up but would not stay running. So i replaced the regulator, now the generator starts but wont stay running and does not blow the fuse. From what i can see looking at the wiring diagram there is a relay made by guardian electric "A410-3666186-151" that takes 120 ac signal to activate a 12 volt relay. That keeps fuel solenoid open.This relay is a 12 pin so I'm not sure how to test it and i have had no luck locating it on the great world wide web.
Hi John,

Are you sure it’s not just an 11 pin relay? (9 pins for 3 sets of double throw contacts and 2 pins for the coil?)

Maybe something like a Potter/Brumfield KUP 14A55 120V

or this Grainger Omron Relay?
http://www.grainger.com/Grainger/OMRON-Square-Base-General-Purpose-Relay-5ZH85?Pid=search
__________________
John Wyatt
Titusville, Florida
1991 40' WLWB-WTB
Body Number F095567
My Location: http://www.bbirdmaps.com/user1.cfm?user=4

1991 40' WB ...From 2008 - Present
1984 ½ PT-36 .From 2000 - 2008
1973 FC-31 .....From 1991 - 2001
Reply With Quote
  #10  
Old 05-30-2011
john wheeler john wheeler is offline
Senior Member
 
Join Date: Nov 2008
Location: Hanford
Posts: 81
Default

Bill
I removed the back cover to look but i cannot find any fuse? Is there a picture of it on the forum

Tom
yes it does run and no (never noticed till now) it is not producing power? i did just install a new regulator

Randy
there is a new solenoid on the starter, i removed the whole control box so i could bench it to have a better look i even tested all the Bosch 5 pin relays which seemed fine. When running i tested the red lead on the fuel solenoid (holding power) and there is no power.
__________________

John wheeler 86 pt38
Hanford,CA
Reply With Quote
Reply

Bookmarks

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
Yanmar/Kohler Problem dslcat Generators 42 07-31-2012 07:08 PM
1990 B.B, 40 ft WB PT Kohler-Yanmar -Gen. Tony Walker Generators 29 07-06-2011 12:57 PM
Kohler Yanmar Oil Drain Plug Torque Spec WestySKPs Generators 8 05-10-2011 09:13 PM
12Kw Kohler generator Yanmar engine zingara1usa Electrical 24 01-11-2011 05:56 PM
Kohler-Yanmar Glow Plug Relay RAGster Generators 4 04-04-2010 04:23 PM

Web Search:

All times are GMT -4. The time now is 03:02 PM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2019, vBulletin Solutions Inc.