On my '82FC35RB with a Kubota/Powertech PTS MH-15BB generator transplant, when I have the engine tank heater turned on it creates an uneven load on the generator and makes it rattle, should the voltage regulator take care of this type of load? Here is the way my breaker panel is labeled and I believe that the engine tank heater is on the front receptacle breaker, has anybody changed the breaker wiring around to compensate for this, or should the voltage regulator just be adjusted to compensate for this?

Attached Thumbnails
Click image for larger version

Name:	ELECTRICAL BREAKER PANEL m.jpg
Views:	556
Size:	118.3 KB
ID:	33578  
__________________

JOHN FINN
FORUM MODERATOR-ADMINISTRATOR
1982 FC35RB
I'm NO EXPERT, but I did stay in the FINN'S INN EXPRESS last night
HOPKINS, SOUTH CAROLINA
VISIT THE FINN'S INN EXPRESS REMODELING ADVENTURE AND TECH. TIPS
I'M SO SLOW ON THE HILLS,THAT I GET TO SMELL THE FLOWERS AS I GO BY.....AND WATCH THEM GROW TOO!! NOT SO MUCH ANYMORE
Visit the WILD HARE RACING website
REMEMBER 9/11

Last edited by iamflagman; 01-14-2015 at 07:12 AM.
Reply With Quote
  #2  
Old 01-14-2015
Bill Pape's Avatar
Bill Pape Bill Pape is offline
Administrator
 
Join Date: Jan 2008
Location: Commerce
Posts: 11,283
Default

As always not a simple question. It is better to have the loads of leg 1 & 2 somewhat balanced, the tank heater is about 1200 /1500 watts, or about 10/12 amps, not enough to throw things off balance,.
More questions are to add up the current draw of each appliance, on each leg, and how you prefer too use the current draw items. The big draw items like block heater, A/C's, electric heaters, hot water, and an occasional microwave use. , If several of the big loads are in use on one leg any large current item could get the loads off balance., but the regulator should compensate for normal usage.
I would be looking for the rattle.
__________________
Bill & Patty
1988 FC, Silver Edition
Commerce, Michigan

Last edited by Bill Pape; 01-14-2015 at 08:37 AM.
Reply With Quote
  #3  
Old 01-14-2015
MarkYuma's Avatar
MarkYuma MarkYuma is offline
Not so Junior anymore
 
Join Date: May 2011
Location: Yuma
Posts: 1,390
Default

The only way I can balance mind is run both Electric heaters the hot water in the engine heater. Then if I want to run the microwave I have to drop off the engine block heater run the microwave and when I'm done cooking during the block heater back on
It's sort of like doing the amp dance with the batteries except different
You can never count on things being wired the same. Or that my hot water heater draws the same correct as yours. That's why it's nice to have it meters on both legs separately and just play with it.
__________________
Mark & Ginger Lauss
Yuma Arizona
1991 PT 40
Towed 1986 Suzuki Samurai OR 2014 Jeep jk
Location: http://www.bbirdmaps.com/user1.cfm?user=259
Reply With Quote
  #4  
Old 01-14-2015
Crit Bliss's Avatar
Crit Bliss Crit Bliss is offline
Senior Member
 
Join Date: Jan 2008
Location: Cape Cod
Posts: 3,921
Default

I would think the rattle is caused by crossing into a higher torque/load range on the engine.
__________________
Crit Bliss
'80FC33
250T
Cape Cod,ma
Reply With Quote
  #5  
Old 08-03-2019
Tailfins57's Avatar
Tailfins57 Tailfins57 is online now
Senior Member
 
Join Date: Sep 2015
Location: Rochester
Posts: 471
Default

Interesting thread that was started by Flynn and captures my own concerns. My PTS MH-15BB GEN begins rattling pretty noticeably when I turn on the air conditioners. It appears to be an imbalance. Gen runs real quiet and smooth until I turn on an air conditioner's. Then it rattles pretty loud. The Gen has had a new bearing. We recently pinpointed a noisy Alternator and a replacement did quiet it down when not under load. But turn on the Air and rattles.
Looking for advice on this, is this typical of Powertech Gens. Concerned that Im blowing it up!
__________________
Dave, Barb,& Dexter Ross
Rochester, MI
BIG Busta Bus
1997 WB43
1977 FC31 RB Sold

"The tallest guy with the shortest bus acquired a "BIG BUSTA"

<bustadesign@hotmail.com>
Reply With Quote
  #6  
Old 08-03-2019
mahansm mahansm is offline
Senior Member
 
Join Date: Apr 2017
Location: Lynn Haven
Posts: 329
Default

The nature of the single phase generator is that the electrical torque loading by the generator head cycles from zero to whatever and back 120 times a second. This creates a torsional vibration on the crankshaft, coupling, and rotor. The more load, the bigger the vibration.
Look at the coupling between the engine and rotor for any play. Look at generator head mountings also.
__________________
Stephen & Kathy Mahan
Bubba & Mattie (malti-poos)

Lynn Haven, Florida
1999 LXi 43 dual slide
Honda CR-V toad

850 814 9022
Reply With Quote
  #7  
Old 08-04-2019
1984Lodge's Avatar
1984Lodge 1984Lodge is offline
Senior Member
 
Join Date: Aug 2017
Location: Temple Terrace
Posts: 373
Default

I have a PTS 12000 powertech generator and have gone through some issues with the uneven loading of 3 air conditioners running. I found out that the generator was wired for 120/240v operation. In this configuration, the generator cannot compensate the voltage for the 110v legs individually, so you end up with the side that is more loaded running at a lower voltage. The only way to compensate for this is to wire the generator to supply only 110v, which is usually possible since there are no 240v loads to supply. I did not notice an increase in the rattling noise that you are talking about though. I may have a totally different engine, I believe mine is a kubota v1505 engine. I am getting ready to check my valve clearances, since I do not know if they have been checked. May be worth checking the valve clearances and see if that is the source of the rattling? If nothing else they should be checked regularly as a part of maintenance anyways.
__________________

Jeff LoGiudice
1984LodgeJeff@gmail.com
Temple Terrace, Florida
1984 Bluebird PT40
#F063411 6V92TA & MT654CR
& 1986 MCI 102A3
6V92TA & HT740

http://www.bbirdmaps.com/index.cfm #460
Reply With Quote
  #8  
Old 08-04-2019
Tailfins57's Avatar
Tailfins57 Tailfins57 is online now
Senior Member
 
Join Date: Sep 2015
Location: Rochester
Posts: 471
Default

Yesterday, I spent some time cycling through different functions and trying to understand what was causing the GEN vibration. I am now convinced it is an overload/ imbalance that is being caused by the AC's.
I am now realizing that a number of things are not right and what made me realize there is a problem was the noise in the GEN. This happens irregularly when AC's are turned on. Watching the Leg 2 gauge, when the noise is happening the gauge is pegging at 35-50 AMPs. The AC is drawing major amps, overloading GEN and creating the imbalance rattle.
I also noticed that my Volt gauges are both reading 135v just up to the RED zone on GEN as well as shore power. Multiple things going on, I will need to spend some more time looking for root cause. Transfer switch is suspect. Looking at other threads around the voltage readings.
__________________
Dave, Barb,& Dexter Ross
Rochester, MI
BIG Busta Bus
1997 WB43
1977 FC31 RB Sold

"The tallest guy with the shortest bus acquired a "BIG BUSTA"

<bustadesign@hotmail.com>
Reply With Quote
  #9  
Old 08-04-2019
Randy Dupree's Avatar
Randy Dupree Randy Dupree is online now
Forum owner
 
Join Date: Dec 2007
Location: Archer,Fl
Posts: 35,170
Default

Make sure your electric heat is off,you may be cooling and heating at the same time.
__________________
DO NOT SEND PM
email me at randy@randydupree.com only.

Randy Dupree
2000 LXI 43
Bainbridge,Ga.
Archer Fl.
www.buybyebluebird.com

randy@randydupree.com
Reply With Quote
  #10  
Old 08-04-2019
brhodes's Avatar
brhodes brhodes is offline
Senior Member
 
Join Date: Nov 2012
Location: Port St. Lucie
Posts: 1,611
Default

Sounds like your HVAC units are starting to have an issue with the START Circuits which need to be replaced as they are not assisting the compressors in starting causing high start current loads.


Transfer switch will not cause a high voltage reading, so look at your shore line voltage source with the coach disconnected and record the reading. Then while disconnected start your generator and allow the transfer switch to come on and with no HVAC's running, see what your voltage is from various wall outlets and compare that to your dash gauges.
__________________
Barry & Mary Rhodes
Port St. Lucie, FL.
1990 WB 40 "Northern Lights"
Body #F92929
brhodes51@yahoo.com
Reply With Quote
Reply

Bookmarks

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
PowerTech Generator, Kubota Voltage Regulator rrueckwald Generators 4 06-10-2013 11:35 AM
15kw powertech makes noise under load Ironbutt62 Generators 27 01-23-2013 04:41 PM
Kubota / Powertech High Temp Shutdown / Thermostat Stuck iamflagman Generators 11 06-30-2012 02:16 PM
FC / Kubota Powertech Transplant Version 2.0 iamflagman 'Bird Projects & Modifications 8 07-18-2011 05:15 PM
Replaced Kohler/Perkins with PowerTech/Kubota jdarst Generators 1 05-11-2008 11:50 AM