Generator voltage measured at outlets inside bus is 155V without load. I would expect it to be higher than 120V unloaded, but this seems higher than it should be. Does anyone have some suggested troubleshooting steps? I would add some loads to see if it drops, but I don't want to chance damaging components with the high voltage. I appreciate any advice that can be provided. Thanks.

Yanmar Model 4TN82E-UK 12.5KW
__________________
Daniel James
Reform, MS
1987 PT40
Reply With Quote
  #2  
Old 01-07-2016
Dave Stokes Dave Stokes is offline
Senior Member
 
Join Date: Oct 2013
Location: Sandy Springs
Posts: 2,921
Default

following since I just discovered a similar problem on leg two with my Powertech 15k
__________________

David & Nicole Stokes and Myla
Atlanta, Georgia
'98 LXi 43'
‘03 LXi 43’ D/S
'00 LXi 43' SS (sold)
'89 WB 40'
2022 Jeep Gladiator Diesel

229-834-8677
Reply With Quote
  #3  
Old 01-07-2016
SNOWBIRD's Avatar
SNOWBIRD SNOWBIRD is offline
Senior Member
 
Join Date: Dec 2015
Location: Lansing
Posts: 929
Default

Voltage is a function of RPMs. Does the genset sound like it is running faster than normal?

Do not run loads at that high voltage.
__________________

Sky Cheney
1998 43' LXi #F119728
Lansing, Michigan
Reply With Quote
  #4  
Old 01-07-2016
konehd konehd is offline
Senior Member
 
Join Date: Jan 2008
Location: Sedona
Posts: 1,821
Default

RPM sets the frequency, voltage is set by the excitation from the voltage regulator...

Dave, if you have high voltage on one leg, whats the other?



/Joe
__________________
Joe & Pat Garner

'93 WB40, Alligator - Sold
Sedona, AZ
Still having fun- even though the the BlueBirds Away!
Reply With Quote
  #5  
Old 01-07-2016
Bill Pape's Avatar
Bill Pape Bill Pape is offline
Administrator
 
Join Date: Jan 2008
Location: Commerce
Posts: 14,672
Default

turn off the power to the bird , 155 is not good it will fry appliances, charger etc. measure both legs at the generator circuit breakers.
__________________
Bill Pape
1988 FC, Silver Edition
Commerce, Michigan
Reply With Quote
  #6  
Old 01-08-2016
danjames danjames is offline
Member
 
Join Date: Jul 2015
Location: Reform
Posts: 57
Default

Raining tonight so I am not going out to troubleshoot. Reviewing generator wiring diagram, it appears problem is most likely in the end bracket area, specifically the automatic voltage regulator. Will check it out this weekend and update this post.
__________________
Daniel James
Reform, MS
1987 PT40
Reply With Quote
  #7  
Old 01-08-2016
danjames danjames is offline
Member
 
Join Date: Jul 2015
Location: Reform
Posts: 57
Default

The generator model is Kohler 12.5CCO67.
__________________
Daniel James
Reform, MS
1987 PT40
Reply With Quote
  #8  
Old 01-08-2016
sfedeli's Avatar
sfedeli sfedeli is offline
Senior Member
 
Join Date: Jan 2008
Location: Sinking Valley
Posts: 3,740
Default

Prior to replacing the regulator, you should check readings across the slip-rings, stator, rotor and individual brushes. The new voltage regulators are not cheap and not very durable. Your Kohler manual has a good flow-chart/troubleshooting guide on pages 7 & 8 for the regulator.
__________________
Shane Fedeli
85PT40
Sinking Valley, PA

"No Bird can soar in a Calm"
shanefedeli@gmail.com
717-645-4912
Reply With Quote
  #9  
Old 01-09-2016
Rick Davis Rick Davis is offline
Senior Member
 
Join Date: Jan 2009
Location: Knoxville, TN
Posts: 2,564
Default

If you find you need to start throwing $$ at replacing parts, you might start saving your pocket change to save up the $1,200 to $3,000 it will take to change the Kohler out to a new brushless solid state head, especially if you plan to keep your Bird.
__________________
Rick & Marilyn Davis
Knoxville, TN
1997 WB43 Mid-door-Sold
1986 PT36 6V92 "Golden Memories"-Sold
1993 WB40 "freeNeasy"-Sold
Reply With Quote
  #10  
Old 01-10-2016
danjames danjames is offline
Member
 
Join Date: Jul 2015
Location: Reform
Posts: 57
Default

Sfedeli,

I have the operation and installation manual but the pages you reference do not have a troubleshooting flowchart or guide. There is a troubleshooting guide in the back of the manual but it is very generic and speaks nothing of the voltage regulator. Would you mind sending me snapshots or PDFs of the pages you have? I would be much obliged. If those documents are already on WOG, please direct me to them. Thanks.
__________________
Daniel James
Reform, MS
1987 PT40
Reply With Quote
Reply

Bookmarks

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
Gennie High Voltage Output Rick Davis Generators 5 04-17-2015 03:10 PM
Basic High Voltage wiring diagram needed '82 PT40 oldmansax Electrical 9 05-24-2011 07:46 AM
No AC Voltage to Coach on generator jwmp Generators 14 05-19-2011 09:36 AM
Onan 8.0 High Voltage Problem K Sarich Generators 10 05-05-2011 09:33 AM
Generator Low Voltage iamflagman Generators 2 02-22-2011 11:08 PM

Web Search:

All times are GMT -4. The time now is 04:05 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.