High generator voltage
Generator voltage measured at outlets inside bus is 155V without load. I would expect it to be higher than 120V unloaded, but this seems higher than it should be. Does anyone have some suggested troubleshooting steps? I would add some loads to see if it drops, but I don't want to chance damaging components with the high voltage. I appreciate any advice that can be provided. Thanks.
Yanmar Model 4TN82E-UK 12.5KW
__________________
Daniel James Reform, MS 1987 PT40 |
#2
|
|||
|
|||
following since I just discovered a similar problem on leg two with my Powertech 15k
__________________
David & Nicole Stokes and Myla Atlanta, Georgia '98 LXi 43' ‘03 LXi 43’ D/S '00 LXi 43' SS (sold) '89 WB 40' 2022 Jeep Gladiator Diesel 229-834-8677 |
#3
|
||||
|
||||
Voltage is a function of RPMs. Does the genset sound like it is running faster than normal?
Do not run loads at that high voltage.
__________________
Sky Cheney 1998 43' LXi #F119728 Lansing, Michigan |
#4
|
|||
|
|||
RPM sets the frequency, voltage is set by the excitation from the voltage regulator...
Dave, if you have high voltage on one leg, whats the other? /Joe
__________________
Joe & Pat Garner '93 WB40, Alligator - Sold Sedona, AZ Still having fun- even though the the BlueBirds Away! |
#5
|
||||
|
||||
turn off the power to the bird , 155 is not good it will fry appliances, charger etc. measure both legs at the generator circuit breakers.
__________________
Bill Pape 1988 FC, Silver Edition Commerce, Michigan |
#6
|
|||
|
|||
Raining tonight so I am not going out to troubleshoot. Reviewing generator wiring diagram, it appears problem is most likely in the end bracket area, specifically the automatic voltage regulator. Will check it out this weekend and update this post.
__________________
Daniel James Reform, MS 1987 PT40 |
#7
|
|||
|
|||
The generator model is Kohler 12.5CCO67.
__________________
Daniel James Reform, MS 1987 PT40 |
#8
|
||||
|
||||
Prior to replacing the regulator, you should check readings across the slip-rings, stator, rotor and individual brushes. The new voltage regulators are not cheap and not very durable. Your Kohler manual has a good flow-chart/troubleshooting guide on pages 7 & 8 for the regulator.
__________________
Shane Fedeli 85PT40 Sinking Valley, PA "No Bird can soar in a Calm" shanefedeli@gmail.com 717-645-4912 |
#9
|
|||
|
|||
If you find you need to start throwing $$ at replacing parts, you might start saving your pocket change to save up the $1,200 to $3,000 it will take to change the Kohler out to a new brushless solid state head, especially if you plan to keep your Bird.
__________________
Rick & Marilyn Davis Knoxville, TN 1997 WB43 Mid-door-Sold 1986 PT36 6V92 "Golden Memories"-Sold 1993 WB40 "freeNeasy"-Sold |
#10
|
|||
|
|||
Sfedeli,
I have the operation and installation manual but the pages you reference do not have a troubleshooting flowchart or guide. There is a troubleshooting guide in the back of the manual but it is very generic and speaks nothing of the voltage regulator. Would you mind sending me snapshots or PDFs of the pages you have? I would be much obliged. If those documents are already on WOG, please direct me to them. Thanks.
__________________
Daniel James Reform, MS 1987 PT40 |
Bookmarks |
Thread Tools | |
|
|
Similar Threads | ||||
Thread | Thread Starter | Forum | Replies | Last Post |
Gennie High Voltage Output | Rick Davis | Generators | 5 | 04-17-2015 03:10 PM |
Basic High Voltage wiring diagram needed '82 PT40 | oldmansax | Electrical | 9 | 05-24-2011 07:46 AM |
No AC Voltage to Coach on generator | jwmp | Generators | 14 | 05-19-2011 09:36 AM |
Onan 8.0 High Voltage Problem | K Sarich | Generators | 10 | 05-05-2011 09:33 AM |
Generator Low Voltage | iamflagman | Generators | 2 | 02-22-2011 11:08 PM |