  #1  
Old 04-17-2019
Dino Dino is offline
The Camel Caravan
 
Join Date: Nov 2018
Location: Reading
Posts: 32
Default Kubota/Powertech generator questions, won't stay running

Hi-- My 15kw Powertech/Kubota generator suddenly won't stay running after start. As long as I hold down the Start switch, the Kubota will start and stay running but as soon as I release the button the engine stops.

Some other forum posts talk about a bad relay that can be bypassed to cure the issue. I assume the relays are in the box I see on top of the generator but I can't get to the box. My power tray seems to work ok but it does not extend enough to be able to see in the box. Is there something wrong with my tray? Can I manualy pull the tray out further?

On the front wall of the driver side front compartment, next to the generator, is a large electrical box. Is that for the generator?

Any help about would be greatly appreciated.
__________________
Dean Hornberger
Reading, Pennsylvania
"The Camel Caravan"
1993 Wanderlodge WB40
Reply With Quote
  #2  
Old 04-17-2019
Kiwi3's Avatar
Kiwi3 Kiwi3 is offline
Senior Member
 
Join Date: Dec 2015
Location: Dothan
Posts: 1,046
Default

Yup that relay should be in the generator fan bay under the driver. If yours is like mine it is the box with the start/stop and the tray in/out switches.
<< Post on the relay >>

You might want to also check that the fuel return valve is open one quarter turn per the manual. Apparently if that is shut off entirely you can end up with some pressure problems that will stall the engine. https://www.wanderlodgeownersgroup.c...ead.php?t=2617

Good luck, and remember I am definitely not a professional.
Attached Files
File Type: pdf PTS-15-25_OPERATORS_MANUAL.pdf (473.8 KB, 23 views)
__________________
Bruce & Marion Griffin
Dothan, AL
1994 Wide Body #106048 "Going Galt"
bruce.griffin67@gmail.com
334-350-8564
Blue Bird Map
Reply With Quote
  #3  
Old 04-17-2019
Dino Dino is offline
The Camel Caravan
 
Join Date: Nov 2018
Location: Reading
Posts: 32
Default Excellent!

Quote:
Originally Posted by Kiwi3 View Post
Yup that relay should be in the generator fan bay under the driver. If yours is like mine it is the box with the start/stop and the tray in/out switches.
<< Post on the relay >>

You might want to also check that the fuel return valve is open one quarter turn per the manual. Apparently if that is shut off entirely you can end up with some pressure problems that will stall the engine. https://www.wanderlodgeownersgroup.c...ead.php?t=2617

Good luck, and remember I am definitely not a professional.
Thank you big time! That makes much more sense then where I thought it was. I'll check on the relay and the fuel return tomorrow.
__________________
Dean Hornberger
Reading, Pennsylvania
"The Camel Caravan"
1993 Wanderlodge WB40
Reply With Quote
  #4  
Old 04-17-2019
NoGas's Avatar
NoGas NoGas is offline
Senior Member
 
Join Date: Apr 2012
Location: DFW & PHX
Posts: 2,129
Default

How’s the generator battery? Years ago my geny battery died, not completely but almost gone. Symptoms were exactly as you describe. New battery and problem fixed. On my coach the geny tray is powered by that batt also. That you’re also having problems with the tray argues for checking the batt.
__________________
Van & Toni in TX & AZ
2004 M380 DS & 2013 Fiat 500 Pop

Last edited by NoGas; 04-17-2019 at 07:46 PM.
Reply With Quote
  #5  
Old 04-18-2019
mburmandds's Avatar
mburmandds mburmandds is offline
Senior Member
 
Join Date: Jan 2011
Location: Bear Valley Springs
Posts: 215
Default

Holding down the run switch provides power to the fuel solenoid that allows fuel delivery from the injection pump, when you let go, the power to the solenoid is interrupted from the run switch but should now be supplied by the oil pressure cut of switch/sender, if the oil pressure is above 3lbs(?). If the sender is faulty or there is insufficient oil pressure, the power to the fuel solenoid is cut-off and the engine dies! The sender is located just above the starter and has 2 wires attached. Here is a link to the sender. https://www.powertechgenerators.com/...hutdown-switch
I think you should be able to check the sender by jumping the two wires together and see if it runs. One of them should have 12v.
There is also a high temp cut-off switch that stops the solenoid when it's too hot.
I think I'm correct on this, but please correct my thoughts if I'm confused!
__________________
Mike and Tami Burman
Bear Valley Springs, CA
1994 40WB
Reply With Quote
  #6  
Old 04-18-2019
Randy Dupree's Avatar
Randy Dupree Randy Dupree is offline
Forum owner
 
Join Date: Dec 2007
Location: Port St Joe,Fl
Posts: 37,012
Default

Quote:
Originally Posted by mburmandds View Post
Holding down the run switch provides power to the fuel solenoid that allows fuel delivery from the injection pump, when you let go, the power to the solenoid is interrupted from the run switch but should now be supplied by the oil pressure cut of switch/sender, if the oil pressure is above 3lbs(?). If the sender is faulty or there is insufficient oil pressure, the power to the fuel solenoid is cut-off and the engine dies! The sender is located just above the starter and has 2 wires attached. Here is a link to the sender. https://www.powertechgenerators.com/...hutdown-switch
I think you should be able to check the sender by jumping the two wires together and see if it runs. One of them should have 12v.
There is also a high temp cut-off switch that stops the solenoid when it's too hot.
I think I'm correct on this, but please correct my thoughts if I'm confused!

Your dead on.
Plus low water can cause this too.
you may have to vent the front upper casting to get the air out.
__________________
DO NOT SEND PM
email me at randy@randydupree.com only.

Randy Dupree
2000 LXI 43
Bainbridge,Ga.
Port St Joe Fl.
www.buybyebluebird.com

randy@randydupree.com
Reply With Quote
  #7  
Old 04-18-2019
arcaidy arcaidy is offline
Senior Member
 
Join Date: Jul 2014
Location: Peachtree City
Posts: 192
Default

Buddy's sob just had a similar issue. It was the run relay. Luckily his start, preheat and run relays were all the same so we just swapped the preheat in to the run and got him going. Don't know if it relates to this gen but figured its worth sharing in case it could.
__________________
James Coffey
Peachtree City, GA
1983 PT35
Reply With Quote
  #8  
Old 05-03-2019
Dino Dino is offline
The Camel Caravan
 
Join Date: Nov 2018
Location: Reading
Posts: 32
Default Update: issue fixed

Thanks for everyone's input. This was caused by the hold/stop solenoid. A new solenoid fixed the problem.

Here is a link to the solenoid I bought on Amazon:
https://www.amazon.com/Blueview-sole.../dp/B079ZYTWM2

I did need to use the plunger and spring from the old solenoid for the new unit to get the proper throw distance and spring pressure.
__________________
Dean Hornberger
Reading, Pennsylvania
"The Camel Caravan"
1993 Wanderlodge WB40
Reply With Quote
  #9  
Old 05-03-2019
GregOC GregOC is offline
.
 
Join Date: Dec 2018
Location: R
Posts: 466
Default

Newer fuel selonids are two efforts in one package. The theory......The black wire is usually ground, red purple pink are usually run and white is usually lift. The red powers parts of the selonoid that does not have enough strength to lift the valve plunger but it will hold open a lifted valve. The white has major strength but draws too many amps and is not rated for continual duty. The operators initial key-on some how powers white momantary which draws many amps to lift the fuel valve. Then while the key is on, the red holds it open.

Looking for the cause of the muffed selonoid I check that the new noid drops power to the white after it starts. In your case it seems like the red is where the issue was. Would be nice to know if signal was dropped or low amp coil was muffed.
__________________
Greg
Reply With Quote
Reply

Bookmarks

Tags
kubota, powertech generator

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
Powertech Generator Kubota 15kw brhodes Generators 10 09-02-2018 09:30 PM
Powertech 15KW won't stay running djlcanuck Generators 6 10-16-2017 09:49 PM
Powertech Generator Parts Kubota 15kw brhodes Generators 0 08-04-2017 01:10 PM
PowerTech Generator, Kubota Voltage Regulator rrueckwald Generators 4 06-10-2013 11:35 AM
Generator won't stay running Mikel Generators 53 10-03-2011 07:21 PM