Default Perkins/Kohler No AC - but fan turning???

More generator problems!

I have a by-pass switch that allows me to run the Perkins when the Generator isn't generating. Gardner helped me while at Birds at the Beach to work around a problem with the controller/regulator that is described in a separate thread. It has worked for a while, but now...

http://www.wanderlodgeownersgroup.co...p?t-16838.html

Now it will only run when the by-pass switch is on (forces the fuel solenoid on). The 220 Volt AC fan is running (maybe slower than usual?). When I switch the manual switch from 50Amp to Gen - nothing. The 2 voltage/polarity gauges don't budge.

I've reset the AC circuit breakers in the generator compartment, and both main circuit breakers in the main circuit breaker box in the bedroom closet.

I've always used the fan turning to indicate that it was generating AC, this time it lies.

Any ideas?

Thanks in Advance.
__________________
Craig Lyndes
'83 FC 35' SB "Bella"
Colchester VT
clyndes@gmail.com
http://blog.livinglearningmobile.com/
Reply With Quote
  #2  
Old 10-03-2015
dmurdock's Avatar
dmurdock dmurdock is offline
Senior Member
 
Join Date: Feb 2013
Location: Cedar Park
Posts: 1,214
Default

I don't think it's lying if I remember correctly the fan is an AC motor (unless it's been changed).
__________________
DuWayne & Shannon Murdock
Cedar Park, Texas
1995 BMC37 Sold
1984 FC35RB Sold
Reply With Quote
  #3  
Old 10-03-2015
gcyeaw's Avatar
gcyeaw gcyeaw is offline
Gardner
 
Join Date: Dec 2007
Location: Ridgewood
Posts: 8,944
Default

Craig,
The control box is near impossible to figure out as the jury-rigged switches and procedures implemented by the PO change everything. Normally once the field is flashed (the B terminal on the reg) the generator needs nothing else to continue producing AC voltage. It does need a working regulator, however, and that might be the problem, but that is a guess.

The fan on mine was a 220 volt unit, now I have a 12 volt one. I don't remember but yours still has the 220 volt AC motor, right?

There are three terminals in the control box for the AC voltage connections. One neutral the two hot leads. Measure the voltage between the neutral and each hot lead, if they are both showing 110-120 then I believe the generator and regulator are working. I know you have to engage the field flash to get voltage (and it drops when you release it now)and you can't hold it on for long, so you need to get creative watching the meter and flashing the field. On my control box the three pole relay is a 110 volt connected between the neutral and one of the hot leads. If this relay is not picking or the contacts are not good it would cause the engine to shut down. But if the engine is running and the field is flashed and the solenoid is engaged the generator should produce voltage till the engine is shut down.

As you probably have read, I gave up on my Kohler and installed a Newage head from Central Georgia Generator. About $1200 with shipping.
It is brushless and does not need the field to be flashed. It does require some mount fabrication and removal of the first muffler(the one next to the Kohler). Mine is actually quieter without it.

My latest new Kohler regulator had 5 wires. One for flashing, two for the brushes (they are + and - and need to be connected to the correct brush.) Two remaining ones go to the two hot leads (one to each lead but not polarized)
__________________
Gardner Yeaw
86 PT-36 Golden Memories
83FC35 SB $IXTEEN TON$ SOLD
78 FC 33 Happinest (Sold)
Ridgewood, New Jersey
Reply With Quote
  #4  
Old 10-03-2015
clyndes's Avatar
clyndes clyndes is offline
Senior Member
 
Join Date: Apr 2009
Location: Colchester
Posts: 343
Default

Thanks folks for your suggestions.

What is really puzzling me is that the 220 Volt AC fan is spinning, but the generator would shut down as if it wasn't able to generate AC and no AC is making it to the panel in the RV.

I have taken apart the control box and see the 3 AC connections in the bottom. Tomorrow, when it is light, I will test those. I have also dug out the replacement for the big ice cube relay that I purchased a while ago and never installed because the spade connectors on it are too big. See the attached picture for my solution. Tomorrow it goes in. I know it does most of the switching in response to there being AC, so I hope it might solve the problem.

Who knows, I might even end up with the original controller working instead of the generic one.

These generators are a pain!
Attached Thumbnails
Click image for larger version

Name:	DSC_0995.jpg
Views:	129
Size:	200.1 KB
ID:	38166  
__________________
Craig Lyndes
'83 FC 35' SB "Bella"
Colchester VT
clyndes@gmail.com
http://blog.livinglearningmobile.com/
Reply With Quote
  #5  
Old 10-04-2015
clyndes's Avatar
clyndes clyndes is offline
Senior Member
 
Join Date: Apr 2009
Location: Colchester
Posts: 343
Default

Spent the weekend replacing all of the relays in the control box.

Results - It is generating AC for both the fan motor and the AC service in the bus. It is no longer running when I do not have the bypass switch on which forces the fuel shutoff solenoid to on. Before this last issue once it was generating AC I could turn the bypass switch off. I think something changed so it is no longer aware that AC is being generated and it can leave the Perkins running.

I have the schematic and need to figure out the circuit that tells it when the AC is on. Does anyone know? The big ice cube relay? Is it switched on by DC or AC?

I took out the $$$ replacement voltage regulator that I had purchased. I was hoping that replacing all the relays would let it work in place of the generic. It didn't work. What I observed is that when the B terminal gets voltage (time to flash the winding) the + wire to the winding gets +12 Volts. I was watching the - wire to the winding for continuity to ground, and instead saw +12 volts!!! Is that what happens when they burn out?

Gardner - I am sad that you switched and no longer have one of these miserable beasts - I'm jealous too!
__________________
Craig Lyndes
'83 FC 35' SB "Bella"
Colchester VT
clyndes@gmail.com
http://blog.livinglearningmobile.com/
Reply With Quote
  #6  
Old 10-04-2015
alvahall's Avatar
alvahall alvahall is offline
Senior Member
 
Join Date: Oct 2008
Location: Cynthiana
Posts: 1,179
Default

Quote:
Originally Posted by clyndes View Post
Spent the weekend replacing all of the relays in the control box.


I have the schematic and need to figure out the circuit that tells it when the AC is on. Does anyone know? The big ice cube relay? Is it switched on by DC or AC?
The CR relay(ice cube)is an AC relay. It is energized by 110V AC from the generator when it is producing the proper voltage. When energized, the CR turns on the "generator is running" light on the start/stop switch and switches the fuel solenoid to the holding coil.
__________________
John & Nancy Hall
Cynthiana, Ky
1988 Narrow PT40
"The Aviary"
Reply With Quote
  #7  
Old 10-05-2015
gcyeaw's Avatar
gcyeaw gcyeaw is offline
Gardner
 
Join Date: Dec 2007
Location: Ridgewood
Posts: 8,944
Default

Craig,
The ice cube picks when there is sufficient AC voltage. One set of points provides 12 volts to the "B" terminal (flash) before the relay picks, and then supplies 12 volts to the 'run' light after it picks. So if the run light lights, the relay is picked. (the last pin, 53, on the terminal block, Blue wire.)

One set of ice cube points when picked energize the 1CR relay that holds the fuel solenoid power.
So identify the 1CR relay and determine if it picks and supplies voltage to the solenoid circuit.

There is no relay on the AC side, so if the fan is running there is AC. If there is AC at the fan there is AC at generator circuit breaker. I don't know what was happening when you had the fan running and no AC in the coach??

Now that you have AC, troubleshooting the control box and determining the issue should get you back to normal operation.

I know in my 83 FC Kohler/Perkins generator there is only one coil in the fuel solenoid. When the start button is engaged it energizes the solenoid. When the ice cube relay picks it routes power to hold the relay. I don't remember if there is another relay involved, but I will look later.

A few years ago I spent $2100 having the generator repaired. Then this year I replaced the regulator and it smoked after 12 hours. It made no sense to fix it again. It was over 30 years old, it was time to move on.
__________________
Gardner Yeaw
86 PT-36 Golden Memories
83FC35 SB $IXTEEN TON$ SOLD
78 FC 33 Happinest (Sold)
Ridgewood, New Jersey

Last edited by gcyeaw; 10-05-2015 at 10:26 AM.
Reply With Quote
Reply

Bookmarks

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
Perkins/Kohler in 79 XV bushdoc Generators 6 05-30-2015 12:39 PM
12.5 Perkins/Kohler Transplant Craig Generators 19 05-27-2015 01:48 PM
perkins kohler genset again Rose Mary Generators 29 12-06-2014 11:20 PM
Perkins Generator Didn't want to stop, now starter keeps turning TKuhlman Generators 40 01-08-2012 02:55 PM
Kohler Perkins - fan direction GPSGary Generators 22 06-04-2009 09:51 PM

Web Search:

All times are GMT -4. The time now is 02:49 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2020, vBulletin Solutions Inc.