Default Main A/C - Generator Selector Switch

I’m not even going to pretend I’m an electric guy (far from it), but in case anyone is interested I shot brief video of what the actual guts of the Generator/Shore Power switch looks like inside the panel. I had no idea it was so, well, big!

https://youtu.be/mIGaQ-teCzs
__________________
Larry Hagen
Kodiak, Alaska
1986 FC35RB

Last edited by Buoy4AK; 11-24-2020 at 12:25 PM.
Reply With Quote
  #2  
Old 11-24-2020
CrashTestDummy's Avatar
CrashTestDummy CrashTestDummy is offline
Senior Member
 
Join Date: Aug 2018
Location: Pearland
Posts: 908
Default

Wow! That is eye-opening. Thanks.
__________________
Barbara and Gene Beaird
Pearland, Texas
1980 FC35 3208NA
Reply With Quote
  #3  
Old 11-24-2020
1984Lodge's Avatar
1984Lodge 1984Lodge is offline
Senior Member
 
Join Date: Aug 2017
Location: Temple Terrace
Posts: 2,416
Default

I am not sure if the OE was Krause Naimer.. but that is who makes those switches now. They are infinitely configurable. As an electrician, we find them in many switchgear for lots of different uses. Generally for selecting voltage and current readings on a meter etc. They use a central shaft and then each module is screwed onto the shaft. Each module can be selected to open or close at a position of the handle. I do not doubt that bluebird ordered these switches to their configuration from a manufacturer similar to this.



Here is the Kraus Naimer website with what would be used to replace these switches:
https://www.krausnaimer.com/us_en/pr...screw-terminal

Here is the catalog that gives you an idea of how configurable these switches are:
https://flippingbook.krausnaimer.com/KN100GB/11/#zoom=z
__________________

Jeff LoGiudice
Jeff@GinosGarageUSA.com
Temple Terrace, Florida
1984 Bluebird PT40
#F063411 6V92TA & MT654CR
& 1986 MCI 102A3
6V92TA & HT740 (Sold)
YouTube-Gino's Garage https://www.youtube.com/user/xjrjeff
http://www.bbirdmaps.com/index.cfm #460
Reply With Quote
  #4  
Old 11-24-2020
Bill Pape's Avatar
Bill Pape Bill Pape is offline
Administrator
 
Join Date: Jan 2008
Location: Commerce
Posts: 13,316
Default

Jeff, Have you ever dismantled and repaired a Switch??
__________________
Bill & Patty
1988 FC, Silver Edition
Commerce, Michigan
Reply With Quote
  #5  
Old 11-24-2020
Randy Dupree's Avatar
Randy Dupree Randy Dupree is offline
Forum owner
 
Join Date: Dec 2007
Location: Port St Joe,Fl
Posts: 43,350
Default

i sold or gave an old burned up switch to Ralph F a long time ago,he said he used it for parts and rebuilt another one.
__________________
DO NOT SEND PM
email me at randy@randydupree.com only.

Randy Dupree
2000 LXI 43
Bainbridge,Ga.
Port St Joe Fl.
www.buybyebluebird.com

randy@randydupree.com
Reply With Quote
  #6  
Old 11-24-2020
1984Lodge's Avatar
1984Lodge 1984Lodge is offline
Senior Member
 
Join Date: Aug 2017
Location: Temple Terrace
Posts: 2,416
Default

Quote:
Originally Posted by Bill Pape View Post
Jeff, Have you ever dismantled and repaired a Switch??
I have had ones apart from switchgear.. but not one from a Wanderlodge, yet. I am sure I they could be fixed if you can get parts for them. They are modular.. so like Randy said if you have old one for parts etc. The big thing with these is whether they are getting corroded or are the contacts in them getting welded due to switching them under load. I do not recommend switching these under load. They can handle a small amount of load but the rating is how much goes through the contacts not the amount of load that can be switched, that is a different number if any is allowed at all.
__________________

Jeff LoGiudice
Jeff@GinosGarageUSA.com
Temple Terrace, Florida
1984 Bluebird PT40
#F063411 6V92TA & MT654CR
& 1986 MCI 102A3
6V92TA & HT740 (Sold)
YouTube-Gino's Garage https://www.youtube.com/user/xjrjeff
http://www.bbirdmaps.com/index.cfm #460
Reply With Quote
  #7  
Old 11-24-2020
Buoy4AK's Avatar
Buoy4AK Buoy4AK is offline
Senior Member
 
Join Date: Jul 2020
Location: Kodiak
Posts: 112
Default

Quote:
Originally Posted by 1984Lodge View Post
I have had ones apart from switchgear.. but not one from a Wanderlodge, yet. I am sure I they could be fixed if you can get parts for them. They are modular.. so like Randy said if you have old one for parts etc. The big thing with these is whether they are getting corroded or are the contacts in them getting welded due to switching them under load. I do not recommend switching these under load. They can handle a small amount of load but the rating is how much goes through the contacts not the amount of load that can be switched, that is a different number if any is allowed at all.
Good to know Jeff! I’ve probably been doing it wrong, when I fire up the genset I leave the selector off then switch to generator after it’s running (which now seems like a bad idea). What do you recommend for procedure when starting the generator? Maybe turning off the AC panel master breaker instead, or maybe just leaving everything on & starting under a load (which also feels like a bad idea)?

Thanks for the feedback!
__________________
Larry Hagen
Kodiak, Alaska
1986 FC35RB
Reply With Quote
  #8  
Old 11-24-2020
78bbird's Avatar
78bbird 78bbird is offline
Senior Member
 
Join Date: Feb 2010
Location: Mariposa
Posts: 1,580
Default

I was able to disassemble and repair the switch in the 78 BB. I have a short write-up here on WOG.
I put the switch to off then start the GEN let it warm up then turn to GEN, back to off then shut down.
__________________
Mark Donahue, Mariposa, CA
1978 FC 33', SB.
donelec@sti.net
2006 Jeep TJ Wrangler X
See my Album!
Reply With Quote
  #9  
Old 11-24-2020
1984Lodge's Avatar
1984Lodge 1984Lodge is offline
Senior Member
 
Join Date: Aug 2017
Location: Temple Terrace
Posts: 2,416
Default

Quote:
Originally Posted by Buoy4AK View Post
Good to know Jeff! I’ve probably been doing it wrong, when I fire up the genset I leave the selector off then switch to generator after it’s running (which now seems like a bad idea). What do you recommend for procedure when starting the generator? Maybe turning off the AC panel master breaker instead, or maybe just leaving everything on & starting under a load (which also feels like a bad idea)?

Thanks for the feedback!
So here are the procedures I use when transferring using the switch:

If you are connecting to shore power or park power:

(If you do not have a power protection device, you may want to check the park pedestal with a meter etc to verify proper power from park outlet. Please only use a meter if you know how to use if properly and safely!)

1.Turn off the breaker at the park power pole.
2.Turn off all your major loads inside the bus, A/C's, water heater etc. the battery charger etc is ok. You could also just flip the main breaker here.
3. Connect your shore power cord and turn the selector switch to 50a or 30a whichever you cord you are connecting.
4. Turn on the park pedestal breaker.
5. Check your polarity meter to make sure power is good.
6. Turn on your loads A/C's etc. Turn on main breaker if you switched it off.

To transfer to generator:
1. Make sure the transfer switch is not on generator yet.
2. Start the generator and let it run for a minute, make sure oil pressure etc is ok.
3. Turn off all the major loads A/C's water heaters etc..as before the small load of battery chargers is usually ok as most take a minute to start drawing load anyways. Could turn off main breaker here.
4. Turn switch to generator, and then start to turn on loads one at a time with a little bit of time in between to let the generator catch up. If you turned off the main breaker, make sure you bring loads in one at a time when on generator power, so turn off all the breakers and bring them in one at a time.
(note its important to not start the generator with large loads turned on, they could see low voltage for the time it takes the generator to get up to speed and some items may not like this and it could damage them)

Transfer from generator back to shore:
1. Turn off all large loads.
2. Turn off park power breaker.
3. Connect shore cord 30a or 50a whichever you have.
4. Switch transfer switch to the 30a or 50a, depending on what you connected to.
5. Turn on park power breaker.
6. Check your polarity meter to verify power.
7. Turn on loads A/C etc.
8. Let generator cool down and then shut it down.
__________________

Jeff LoGiudice
Jeff@GinosGarageUSA.com
Temple Terrace, Florida
1984 Bluebird PT40
#F063411 6V92TA & MT654CR
& 1986 MCI 102A3
6V92TA & HT740 (Sold)
YouTube-Gino's Garage https://www.youtube.com/user/xjrjeff
http://www.bbirdmaps.com/index.cfm #460
Reply With Quote
  #10  
Old 11-24-2020
ChrisRasman's Avatar
ChrisRasman ChrisRasman is offline
Senior Member
 
Join Date: Jun 2019
Location: Fort Myers
Posts: 1,826
Default

Bless my automatic transfer switch lol.

The rotary power switch is common and on Amazon. The contactors are easy out of old AC condensers or cheap online.

https://www.amazon.com/gp/product/B0...?ie=UTF8&psc=1
__________________
Christopher Rasmussen
USN Ret
Fort Myers, FLORIDA
2003 Wanderlodge 40LX
Body# F133835
Reply With Quote
Reply

Bookmarks

Tags
buoy4ak, fc35rb

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
97 WLWB Battery Selector Switch problem Bigal87 General 14 08-30-2016 02:18 PM
Shore power selector switch MattT Electrical 3 06-24-2016 08:56 PM
transmission selector switch - no reverse! Mikenjackie PT & WB (Twin Axle Pusher Unique Issues) 7 04-18-2014 02:08 PM
Selector Switch Antenna Satellite VCR drdonny General 4 09-03-2013 10:35 AM
AC Power Selector Switch Jerry_94110 Generators 13 05-31-2011 01:16 PM

Web Search:

All times are GMT -4. The time now is 06:53 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2022, vBulletin Solutions Inc.